Trains.com

New AMTRAK, CALIFORNIA HSR train sets

6228 views
18 replies
1 rating 2 rating 3 rating 4 rating 5 rating
  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
New AMTRAK, CALIFORNIA HSR train sets
Posted by blue streak 1 on Thursday, January 17, 2013 6:20 PM

The announcement of a joint procurement of hHSR train sets had 2 very interesting points.  Here is a snippet of the AMTRAK statementi 

"" In addition, the preferred train set has Electric Multiple Unit (EMU) power distribution among all cars, operates bi-directionally with a cab car on each end that allows for passenger occupancy and has a seating capacity of 400 to 600 passengers. ""

Using EMU power distribution is most important for AMTRAK.  The potential for quicker acceleration and deccelaration will enable AMTRAK to operate on the NEC quicker with its many slower sections.    IMO the EMU operation vs a locomotive / motor would probably save 10 - 15  minutes on the NEC   NYP - WASH   at the present time ?? AS each  NEC  slow section is eliminated the timekeeping will naturally improve. Note also the press release says that the first new trains will be for additional service. 

Also note the apparent increase of AMTRAK passenge capacity to 600.  That would almost double the present ACELA' s  300 + passengers instead of the dropped proposal of adding 2 business class coaches to present ACELAs.  So will this be called a  "Super ACELA"?

The need for much smaller HP traction motors under each car would reduce the unsprung weight on axels that many of you posters have noted causes problems.  will reduce track maintenance.

CA HSR will not get as much benefit from the EMU traction setup since most of its ROW will be built to either 220 where easy or 160 MPH at difficult places ?

One result of the 160 MPH tests may be this decision to get EMU type traction.  How many contact PANs will be on the trains is anyone's guess.

Here is the AMTRAK RELEASE;

http://www.amtrak.com/ccurl/620/710/Amtrak-CHSRA-Joint-RFI-HSR-Train-Sets-ATK-13-012.pdf

 

  • Member since
    August 2012
  • 3,727 posts
Posted by John WR on Thursday, January 17, 2013 6:54 PM

The benefits of multiple units--the ability to tailor power to the weight of the train and the fact that with several traction motors each one is much lighter than a single or double one would be--have long been known.  I wonder why these were not incorporated into the present day Acela.  

California is a single state which an make a single decision for high speed rail on a line that will ultimately be 800 miles long.  No state on the northeast corridor can possibly do that.  New York could do it between  New York City and Buffalo and Pennsylvania could do it between Philadelphia and Pittsburgh.  However, I guess they are still not inclined to do so.  

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Thursday, January 17, 2013 7:19 PM

Several more points.

1. Bi - directional 

a.  NEC  --  BOS, NYP, WASH---  PHL for turns to HARRISBURG

b.  CA  --   SACREMENTO,  SFO new transbay terminal, SAN DIEGO,  LAX  until run thru at station is built

2.   Cab cars with seating  --  keeps train sets shorter for given capacity especially important at NYP until new tunnels and expansion of station is built.

3.  Wonder  if the CA trains will uses the same transformer that will be needed for the NEC 25 Hz ? note ; 25 Hz transformer will work on 60 Hz but 60 Hz cannot work on 25 without major degregation.

  • Member since
    September 2011
  • 6,449 posts
Posted by MidlandMike on Thursday, January 17, 2013 8:52 PM

Good point about 60 Hz vs 25 Hz.  Amtrak will never be able to buy  "off the shelf" until they convert to 60 Hz.

  • Member since
    August 2012
  • 3,727 posts
Posted by John WR on Thursday, January 17, 2013 9:09 PM

MidlandMike
Good point about 60 Hz vs 25 Hz.  Amtrak will never be able to buy  "off the shelf" until they convert to 60 Hz

But with today's electronic converters all kinds of conversion seems simple.  Right now some systems take AC, convert it to DC in the locomotive and then convert it back to some other AC frequency often with a square wave.  

In the northeast Amtrak still used some electromechanical converters because it has them.  But as time goes on it has to replace them with electronic converters.  

  • Member since
    January 2001
  • From: Atlanta
  • 11,971 posts
Posted by oltmannd on Friday, January 18, 2013 9:30 AM

MidlandMike

Good point about 60 Hz vs 25 Hz.  Amtrak will never be able to buy  "off the shelf" until they convert to 60 Hz.

It's just the transformer.  Amtrak ran an "off the shelf" Rc4 (AEM7), X2000 train set, ICE (gen 1) trainset.  These were all returned to Europe and placed in service there. Couldn't be a huge deal....

-Don (Random stuff, mostly about trains - what else? http://blerfblog.blogspot.com/

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Friday, January 18, 2013 12:38 PM

oltmannd

It's just the transformer.  Amtrak ran an "off the shelf" Rc4 (AEM7), X2000 train set, ICE (gen 1) trainset.  These were all returned to Europe and placed in service there. Couldn't be a huge deal....

This is just speculation at this point in time but it probably will be transformers in each train car.  If cab cars are going to be at each end then we may see a power car with PANS in the middle of the train set.  I have seen pictures of some european train sets with that design.
Assuming   AC  traction motors  -------
1.  Then either a single transformer could be in the power car with a power cables jumpered on roof to each car.  The cables could provide either DC with inverters in each car ---  OR  AC with a single  traction control inverter  but either option would take rather large cables.
2.  Or ---  there may be just a single high voltage jumper -- car to car --  with a much smaller transformer compartment  in each car along with rectifier and inverters. That would be much like present day EMUs which technology is well proven.   
3.  With either option a 25 Hz / 60 Hz transformer will be required for AMTRAK.  Probably a center tap transformer for both as station CAT has many advantages of being 12.5 Kv. for example NYP with it close clearances could never be 25 Kv.
4.  CA can use only a 60 Hz transformer but if any units were to be capable of operating on both coasts then simply installing a dual frequency transformer will be easy. Dual voltage transformer is still very useable fo CA.
5.  The dual frequency transformers will be almost 2 - 1/2 times bigger than a 60 Hz only transformer but in the EMU cars will probably weigh only about 500#s more ?
6.  Option #2 may enable AMTRAK & CA  to change train set lengths fairly easily ?. 
  • Member since
    August 2012
  • 3,727 posts
Posted by John WR on Friday, January 18, 2013 4:32 PM

blue streak 1

How many contact PANs will be on the trains is anyone's guess.

Right now on MU's it is common to run married pair cars that have a pantograph on every other car.  

  • Member since
    September 2011
  • 6,449 posts
Posted by MidlandMike on Friday, January 18, 2013 8:58 PM

John WR

MidlandMike
Good point about 60 Hz vs 25 Hz.  Amtrak will never be able to buy  "off the shelf" until they convert to 60 Hz

But with today's electronic converters all kinds of conversion seems simple.  Right now some systems take AC, convert it to DC in the locomotive and then convert it back to some other AC frequency often with a square wave.  

In the northeast Amtrak still used some electromechanical converters because it has them.  But as time goes on it has to replace them with electronic converters.  

And the reason to buy and maintain this extra layer of electronics, is why?

  • Member since
    December 2005
  • From: Cardiff, CA
  • 2,930 posts
Posted by erikem on Saturday, January 19, 2013 9:38 AM

Not sure about which layer of electronics you were referring to, so will attempt to answer both.

Converting from (single phase, fixed voltage and frequency) AC to DC and then back to (three phase variable voltage and frequency) AC is to use of induction motors. Chances are you already knew that.

Converting from three phase 60 Hz to single phase 25 Hz is to accommodate the existing catenary and related power distribution equipment. For a given voltage, more power can be delivered to a train at 25 Hz than at 60 Hz, due to the effects of inductive reactance (scales with frequency) and skin effect (scales with the square root of frequency). In the short term, it may be cheaper to replace the rotating frequency converters with static converters than to replace the catenary and associated electrical gear.

- Erik

  • Member since
    August 2012
  • 3,727 posts
Posted by John WR on Saturday, January 19, 2013 3:30 PM

Perhaps I am missing something, Erik.  All of the jumping back and forth between 60 and 25 boggles my mind.  

I understand that the New Haven Railroad when it electrified between New York and New Haven set up the system to use 25 Hz and that that time 25 Hz was easily available.

Today it is not available or it is less available so Amtrak has to deal with that.  They deal with it by converting from 60 Hz to DC to 25 Hz because that is the most practical way to do it.  

Am I wrong on this?

 

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Saturday, January 19, 2013 6:49 PM

John WR

Today 25Hz is not available or it is less available so Amtrak has to deal with that.  They deal with it by converting from 60 Hz to DC to 25 Hz because that is the most practical way to do it.  

Am I wrong on this?

 

afraid so ---  no DC INVOLVED

3 ways now ---

1. The old PRR method using what is called a rotary converter which looks like an overgrown motor without any shaft but just 60 Hz wires in and 25 Hz  out.

2..  Motor generator sets  60 Hz electric motor connected by shaft to a 25 Hz generator. 

 note;    both #s 1 & 2 rotate at a common  divisor  speed of 3600 & 1500   ( freq times 60 RPM times electric frequency ). (highest speed 300 RPM next 150 RPM)

3.  A solid state converter  ---   method or  mechanism unknown.

MNRR  changed the NH route to 60 Hz due to failures of COS COB power station.  The change over was much simpler than a conversion of the PRR section will be due to much more PRR equipment tied to25 Hz. Even so it took over 2 weekends and a full week to complete. That was just the time there was no electric service by MNRR or AMTRAK only diesel.  EMUs were started converting a month or so before and were not completed for almost 2 months.  Someone have more details ? 

there was a long thread a year or more ago that went into this in detail

  • Member since
    September 2011
  • 6,449 posts
Posted by MidlandMike on Saturday, January 19, 2013 10:57 PM

erikem

...

Converting from three phase 60 Hz to single phase 25 Hz is to accommodate the existing catenary and related power distribution equipment. For a given voltage, more power can be delivered to a train at 25 Hz than at 60 Hz, due to the effects of inductive reactance (scales with frequency) and skin effect (scales with the square root of frequency). In the short term, it may be cheaper to replace the rotating frequency converters with static converters than to replace the catenary and associated electrical gear.

- Erik

I am guessing you are right about it being cheaper to replace the rotary converters than to change the cat, which is probably why Amtrak did that and put off their planned frequency and cat change.  Nevertheless, the present fixed cat is not appropriate for high speed, and will eventually need upgrading.  In the meantime they must deal with all the 25 Hz obsolescence problems. 

  • Member since
    December 2005
  • From: Cardiff, CA
  • 2,930 posts
Posted by erikem on Sunday, January 20, 2013 1:45 AM

blue streak 1

John WR

Today 25Hz is not available or it is less available so Amtrak has to deal with that.  They deal with it by converting from 60 Hz to DC to 25 Hz because that is the most practical way to do it.  

Am I wrong on this?

 

afraid so ---  no DC INVOLVED

3 ways now ---

1. The old PRR method using what is called a rotary converter which looks like an overgrown motor without any shaft but just 60 Hz wires in and 25 Hz  out.

2..  Motor generator sets  60 Hz electric motor connected by shaft to a 25 Hz generator. 

 note;    both #s 1 & 2 rotate at a common  divisor  speed of 3600 & 1500   ( freq times 60 RPM times electric frequency ). (highest speed 300 RPM next 150 RPM)

The PRR used #2, the rotary converters (AKA synchronous converters) were used for converting AC to DC. "Motor generator set" is slightly misleading, they're actually two synchronous machines that can act as either a motor or generator. Most of the time the 60 Hz machine is the "motor" and the 25 Hz machine is the "generator".


3.  A solid state converter  ---   method or  mechanism unknown.

25 Hz is too close to 60 Hz for a cycloconverter to work well, the 1:3 ratio in Europe is more conducive to cycloconverter operation. FWIW, a cycloconverter does a direct conversion of one AC frequency to another that is 1/3 or less of the first frequency.

I would strongly suspect that static (i.e., no moving parts) converters do transform to DC then back to AC. One reason is giving a well balanced three phase load and another is allowing more freedom in ratio of input and output frequencies.  FWIW power companies make use of AC to DC to AC interties to allow power to be transferred asynchronously between two grids (such as between the west coast and east coast, though GE has developed a phase shifting transformer that may be more efficient.

- Erik

  • Member since
    January 2001
  • From: Atlanta
  • 11,971 posts
Posted by oltmannd on Sunday, January 20, 2013 7:47 AM

Is there any equipment left on the NEC that is not dual-frequency?  Perhaps, as the new cat is strung, it could be powered by the same freq and voltage as the north end of the NEC.

I seem to remember that the NJT Arrows can't switch on the fly.  Perhaps they could be restricted to Hoboken trains.

-Don (Random stuff, mostly about trains - what else? http://blerfblog.blogspot.com/

  • Member since
    June 2009
  • From: Dallas, TX
  • 6,952 posts
Posted by CMStPnP on Sunday, January 20, 2013 9:27 AM

I think it is great Amtrak is finally setting standards on HSR trainsets, Corridor Cars and hopefully soon Commuter cars.     If we get one basic nationwide design we all save substantial taxpayer money on the orders and  maintenence, IMO.    No restriction on the amount of tweaks to the platform but the basic platform should be the same across the country, IMHO.

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Sunday, January 20, 2013 9:51 AM

erikem

 One reason is giving a well balanced three phase load and another is allowing more freedom in ratio of input and output frequencies.  FWIW power companies make use of AC to DC to AC interties to allow power to be transferred asynchronously between two grids (such as between the west coast and east coast, though GE has developed a phase shifting transformer that may be more efficient.

- Erik

Erik; 
One item that I have never quite understood is the PRR method of high voltage transmission.  Those lines are powered not 3 phase but much like our houses.  The lines are single phase in pairs with each line 69 KV to ground and 138 Kv line to line. This may have been for use of auto transformers to CAT voltages ?  At those locations on AMTRAK where there are 4 or 6 transmission lines they may be split phase or 3 phase ?   That transmission method may be another problem impeeding conversion of parts of the NEC at a time to 60 HZ ?.  Might require expansion of transmission system ? Wonder how the Safe Harbor 25 Hz generators are wired ? Any 3 phase lines now on the ROW belong to the local utility by is easement and not belonging to AMTRAK.
This method may have been the best available at the time the first section was built.  However I have never been able to confirm or deny that the NHRR 25 Hz that was started before PRR was transmitted 3 phase ?  Does anyone have any reference either way ?
 
  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Sunday, January 20, 2013 11:05 AM

oltmannd

Is there any equipment left on the NEC that is not dual-frequency?  Perhaps, as the new cat is strung, it could be powered by the same freq and voltage as the north end of the NEC.

I seem to remember that the NJT Arrows can't switch on the fly.  Perhaps they could be restricted to Hoboken trains.

Lets see----- 
AMTRAK  motors  --   All dual frequency and dual voltage 12Kv 25 Hz, 12.5 Kv 60 Hz, 25 Kv 60 Hz.
MARC motors  --  same as AMTRAK but not sure of the 25 KV 60 Hz ?
SEPTA  ---   SILVER LINERS 2s, 3s, 4s  --   25 Hz only.  DC traction ,  as well all auxiliaries are 25 Hz
                      SILVER LINER 5s  ---   Yes all 3 power sources. They have center tap transformers for 25 Kv.  Auto switching equipment is not installed but has provision for installation by SEPTA.
              ---     Motors   --   Same as MARC motors.
NJ TRANSIT  --  Motors  --  ALP44s  --  Same as MARC motors.
                        --                     ALP45DPs, ALP46s  --   Same as AMTRAK motors
                            EMUs   ---   Some may still be only 25 Hz ( would depend if any auxiliaries 25 Hz ), some 25 & 60 Hz with manual switching both voltages, some same as AMTRAK motors.
MNRR  ---  M2, M4, M6s all converted to 60 Hz when track was converted to 60 Hz but unknown if can operate on 25 Kv or 25 Hz.
             -----   M8s  --  operate on 60 Hz 12.5 Kv, 25 Kv 60 Hz only.  Do not  have a 25 Hz capable transformer.  This will cause a major problem preventing MNRR service from New Haven to NYP. NYP CANNOT  be converted to 12.5 Kv 60 Hz until the problem of NJ TRANSIT's inability to switch on the fly is solved.
 
The reason for all the confusing differences ?. 
1.  If the power take offs from the transformers go directly to auxiliaries & DC traction rectifiers then those cannot operate on dual frequencys.
2.  If an EMU uses rectified current for DC and for auxiliaries can allow dual freq AC to operate unit  . How flourescent lights are powered is unknown.
3.  When the motors and EMUs use a 25 Hz capable transformer, then rectifies the output, then sends the DC to inverters and output both variable freq for the AC traction motors and constant freq power for all auxiliaries then can run on both frequencies.  12kV 25 hz and 12.5 KV 60 Hz close enough in voltage so no problem.  CENTER TAP transformers work great as they tap center for 12 Kv and end for 25 Kv.  
Clear as mud ???
   
          
  • Member since
    December 2005
  • From: Cardiff, CA
  • 2,930 posts
Posted by erikem on Sunday, January 20, 2013 11:23 AM

Reasonable questions.

The 25 Hz power is generated by three phase alternators connected to produce single phase, the same way the 25 Hz plants owned by the New Haven, N&W and Virgininian were set up. There were slight modifications made to the alternators to accommodate the phase imbalance.

The 25 Hz power on the PRR is transmitted as single phase, the plus/minus 69kV arrangement is to both minimize the insulation requirements and to keep currents in the conductors balanced to minimize unwanted inductive effects (i.e. where current is induced in other conductors, e.g. telephone lines). The PRR had multiple circuits for redundancy, each pair of wires was one circuit.

I don't think the PRR used autotransformers, as those are more appropriate with a 2:1 voltage ratio as used on the New Haven.

- Erik