WMATA to Stop Operations Tomorrow
Posted by Buslist on Tuesday, March 15, 2016 10:35 PM

Word is that the WMATA rail system will not operate tomorrow. This will permit a complete inspection of traction power feeder cables. One of these cables was blamed for a fire in the subway a few months ago. At this time it's unclear what triggered the inspection at this point. This should making commuting in DC real fun tomorrow.

  • Member since
    May 2003
  • From: US
  • 25,292 posts
Posted by BaltACD on Tuesday, March 15, 2016 10:36 PM

Buslist

Word is that the WMATA rail system will not operate tomorrow. This will permit a complete inspection of traction power feeder cables. One of these cables was blamed for a fire in the subway a few months ago. At this time it's unclear what triggered the inspection at this point. This should making commuting in DC real fun tomorrow.

What triggered the shut down was a fire on the 14th of this month that was similar to the one last year that ended up killing one person.  The 14ths fire affected 3 of Metro's lines.

Never too old to have a happy childhood!

              

  • Member since
    August 2006
  • From: South Dakota
  • 1,592 posts
Posted by Dakguy201 on Wednesday, March 16, 2016 10:17 AM

I'm having trouble understanding (assuming these cables are routinely inspected) why a no-notice inspection had to be made.  Could this not have waited long enough to give the public time to plan for the outage or to do the outage on a weekend?  Is my inspection assumption wrong, even after last year's incident?  

  • Member since
    May 2003
  • From: US
  • 25,292 posts
Posted by BaltACD on Wednesday, March 16, 2016 10:57 AM

In today's enviornment you can never downplay the 'S' word; especially in DC.  In the past WMATA has played very loose with the 'S' word - to their detriment.

Never too old to have a happy childhood!

              

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Wednesday, March 16, 2016 11:50 AM

So all 3rd rail power will be shut down at sub stations.  Question what feeders ?

1.  Feeders from power sub station to distribution nodes ?

2.  Connectors at nodes to 3rd rail cable ?

3.  Bad third rail cable ?

4.  3rd rail cable connection to 3rd rail ?

 5.  Ground connections to  running rails ?

6.  Any other ? 

Will / Can we find out if it was caused by poor materials or poor workmanship ?

 

  • Member since
    May 2003
  • From: US
  • 25,292 posts
Posted by BaltACD on Wednesday, March 16, 2016 12:03 PM

blue streak 1

So all 3rd rail power will be shut down at sub stations.  Question what feeders ?

1.  Feeders from power sub station to distribution nodes ?

2.  Connectors at nodes to 3rd rail cable ?

3.  Bad third rail cable ?

4.  3rd rail cable connection to 3rd rail ?

 5.  Ground connections to  running rails ?

6.  Any other ? 

Will / Can we find out if it was caused by poor materials or poor workmanship ?

7. or age?

Never too old to have a happy childhood!

              

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Wednesday, March 16, 2016 2:14 PM

Balt agree some of it could be age but those electric cables ahould still have a lot of life. ( unless improper cables snuck in ) However if improper inspection of feeders occurred then loose connections will certainly age supply cables faster.  Know an electrician whose sole job is during 3rd shift shutdowns to check that all connections are tight.  He does say loose connections will raise havoc with computers. 

  • Member since
    November 2005
  • From: Hope, AR
  • 2,061 posts
Posted by narig01 on Wednesday, March 16, 2016 2:17 PM

Considering the criticism WMATA has received in past it is good to hear that WMATA is willing to take the extreme step of a maintenance stand down. It may be an overreaction, however better safe the sorry. 

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Wednesday, March 16, 2016 2:25 PM

If this shutdown inspection results in a few terminations of employees then the whole system will get the message that they best do their jobs ?

  • Member since
    March 2016
  • 1 posts
Posted by CandOforprogress on Wednesday, March 16, 2016 3:30 PM
Another case of the government being in a total disconnect with the people
  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Wednesday, March 16, 2016 6:02 PM

Just saw a CBS report on the shutdown.  A picture showed the cables from the nodes to the 3rd rail severely open and some of the braids of the cable broken.  Just speculation but the one showed may have overheated melting the insulation and then the copper braids ?  Not always but that may indicate loose connections at nodes or 3rd rail..

But the most damming of the report said 26 problems were found.  Now how could that many be missed except for either sloppy inspections or incompetent management ?   Fire some people ! ! ! These problems will probaly need correcting before service through each problem section can be restored. ?

Maybe an NTSB investigation ?

  • Member since
    May 2003
  • From: US
  • 25,292 posts
Posted by BaltACD on Wednesday, March 16, 2016 6:15 PM

blue streak 1

Just saw a CBS report on the shutdown.  A picture showed the cables from the nodes to the 3rd rail severely open and some of the braids of the cable broken.  Just speculation but the one showed may have overheated melting the insulation and then the copper braids ?  Not always but that may indicate loose connections at nodes or 3rd rail..

But the most damming of the report said 26 problems were found.  Now how could that many be missed except for either sloppy inspections or incompetent management ?   Fire some people ! ! ! These problems will probaly need correcting before service through each problem section can be restored. ?

Maybe an NTSB investigation ?

Safety problems start at the top of the Command Structure, not at the bottom.  You either develop a safety culture within the organization or everyone from the CEO gets sloppy and views safety as a red headed step child.  WMATA has been such a organization. 

Never too old to have a happy childhood!

              

  • Member since
    August 2006
  • From: South Dakota
  • 1,592 posts
Posted by Dakguy201 on Wednesday, March 16, 2016 6:18 PM

blue streak 1

Just saw a CBS report on the shutdown.  A picture showed the cables from the nodes to the 3rd rail severely open and some of the braids of the cable broken.  Just speculation but the one showed may have overheated melting the insulation and then the copper braids ?  Not always but that may indicate loose connections at nodes or 3rd rail..

But the most damming of the report said 26 problems were found.  Now how could that many be missed except for either sloppy inspections or incompetent management ?   Fire some people ! ! ! These problems will probaly need correcting before service through each problem section can be restored. ?

I obtained much the same news from another source.  However, there was no mention of any immediate corrective actions being taken.  The system will start running again at 5 tomorrow morning.

So now that they know there are defects, some serious, they are going to resume operations?  Have you seen the TV commercial with the individual who is not a security guard, but a security monitor?  He monitors the situation and reports, sure enough, there is a bank robbery in progress.  It appears riders of this system are in the same situation as that bank's customers.

(Edited to add):

As the video below makes clear, they did make fixes as defects were found. 

  • Member since
    November 2005
  • 4,190 posts
Posted by wanswheel on Wednesday, March 16, 2016 6:52 PM

  • Member since
    November 2005
  • From: Hope, AR
  • 2,061 posts
Posted by narig01 on Thursday, March 17, 2016 1:42 PM

BaltACD

 

 
blue streak 1

Just saw a CBS report on the shutdown.  A picture showed the cables from the nodes to the 3rd rail severely open and some of the braids of the cable broken.  Just speculation but the one showed may have overheated melting the insulation and then the copper braids ?  Not always but that may indicate loose connections at nodes or 3rd rail..

But the most damming of the report said 26 problems were found.  Now how could that many be missed except for either sloppy inspections or incompetent management ?   Fire some people ! ! ! These problems will probaly need correcting before service through each problem section can be restored. ?

Maybe an NTSB investigation ?

 

Safety problems start at the top of the Command Structure, not at the bottom.  You either develop a safety culture within the organization or everyone from the CEO gets sloppy and views safety as a red headed step child.  WMATA has been such a organization. 

 

In this case the NTSB has made any number of comments about WMATA' s lack of safety culture, and further said that WMATA lacked outside sources of safety oversight. IE regulatory agencies that could order change. This is an important check against unbounded government. It is also another layer of bureaucracy, that the last 30+ years of Washington politics has abhorred. Just firing people willy nilly has very little effect if their replacements don't have effective supervision and management. And the memory of what went wrong.(both mechanically and people wise)

    

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Thursday, March 17, 2016 3:37 PM
  • Member since
    February 2005
  • 120 posts
Posted by bartman-tn on Thursday, March 17, 2016 6:05 PM

According to Progressive Railroading this morning..."All but four of the defective locations have been remedied as of last night."

  • Member since
    May 2003
  • From: US
  • 25,292 posts
Posted by BaltACD on Thursday, March 17, 2016 6:12 PM

blue streak 1

Many political organizations in the DC area required a wake up call about Metro's importance to the area as well as it's need for stable funding.  Maybe they got the message, maybe they didn't.  Time will tell.

Never too old to have a happy childhood!

              

  • Member since
    February 2005
  • 120 posts
Posted by bartman-tn on Thursday, March 17, 2016 8:30 PM

Having worked several projects for WMATA, in my opinion funding is not the problem, it is how it is managed by a number of people with no rail transit experience, who have never seen a system long enough to see parts failed, and a rigid process that cannot respond to changes in its infrastructure. The process to repair just a simple problem can require several departments to coordinate activities and personnel, with many cases having no clear responsibility or authority.  The NTSB's report found many of the same problems.

  • Member since
    December 2007
  • From: Georgia USA SW of Atlanta
  • 11,919 posts
Posted by blue streak 1 on Tuesday, July 5, 2016 8:55 PM

These fires have been blamed on bad insulators.  METRO announces all porcelian insulators have been replaced by fiberglass insulators.

http://www.progressiverailroading.com/safety/news/WMATA-replaces-porcelain-third-rail-insulators--48699

Why has no other agency have problems with their insulators ?  Porcelain is just a ceramic.  Remember all atmosphere re entry vehicles have ceramic tiles and nose cones. 

Question.  did the specifications not have a high enough temp threashold ? .  Did insulator manufacturer either not report that specification were too low or did it build faulty insulators. ?

 Another article with a picture.

 http://www.rtands.com/index.php/passenger/rapid-transit-light-rail/wmata-completes-installation-of-fiberglass-insulators.html?channel

  • Member since
    November 2005
  • From: Hope, AR
  • 2,061 posts
Posted by narig01 on Thursday, July 7, 2016 10:39 PM

I was looking at the video from March showing the damaged shunt cables connecting the third rail. What I can not understand is this,

The cable has insulation cracked but I did not see any signs of excessive heat(ie melted insulation). What I saw looks more like something hit the cable and tore the insulation. Also is it standard practice to have the shunt cable on the same side that the third rail shoe travels on? It occurs to me that if the third rail shoe caught a piece of debris it could very easily have torn the insulation. 

      Further I have to wonder aloud about the porcelain insulators. The pictures I saw of the old insulators showed dirty insulators. Another words no one was on occasion cleaning them. Fibreglass is made with resin which given a chance will burn. Porcelain has already been fired in the manufacturing process. 

Not sure what else to say.

  • Member since
    May 2013
  • 3,231 posts
Posted by NorthWest on Friday, July 8, 2016 12:05 AM

My possibly warped understanding is that the apparently conductive debris allowed the third rail to arc to the metal post holding the insulator, melting it. Fiberglass insulators are supposed to handle heat better, but the real solution is for Metro to actually clean their tunnels.

  • Member since
    September 2008
  • 1,112 posts
Posted by aegrotatio on Wednesday, July 13, 2016 9:53 PM

The bad insulators are a separate problem. The original concern, and the reason for the one-day shutdown, was for insulating boots on feeder cables that were either not installed properly or were at the risk of failing due to wear or other reasons.

 

The insulator problem is a separate problem. These are the ceramic pedestals that hold the third rail and were quickly replaced only at every *station* because of a high-profile video which shows a fireball showering the tracks and part of the station platform with sparks and fire just after a train departed the station. The insulators in the tunnels are still in the process of being replaced but the insulators inside the stations were a priority for obvious reasons. Most of these insulators are original and many are 30-40 years old.