Trains.com

Subscriber & Member Login

Login, or register today to interact in our online community, comment on articles, receive our newsletter, manage your account online and more!

Building a train room?

1444 views
14 replies
1 rating 2 rating 3 rating 4 rating 5 rating
  • Member since
    April 2007
  • From: Ontario
  • 737 posts
Posted by da_kraut on Wednesday, April 2, 2008 7:28 PM

HI, welcome to the forum.

Here is another location in the forum where this question was asked,

http://cs.trains.com/forums/1264406/ShowPost.aspx .

Hope it helps.

 

Frank 

"If you need a helping hand, you'll find one at the end of your arm."

  • Member since
    July 2004
  • From: Weymouth, Ma.
  • 5,199 posts
Posted by bogp40 on Wednesday, April 2, 2008 5:39 PM

For an out building/ shed of that size you don't need a 100A service unless your city or town requires it.

Codes and requirements will vary to location. If your jurisdiction allows homeowners to do electrical work and you feel confident enough to handle the task then do so. From your initial question as to unclear what your power needs and breakers, you should be contacting a licensed electrician. Many insurance companies will also frown on this work done by a non qualified individual. Just needed to throw this out there, I don't know the circumstances.

Now as to electrical needs: If your residential service is at least 100A and the busses are not maxed out due to house needs (full electric house,or electric dryer,water heater, AC and range), it may be possible to add a 40-50A 220 breaker controlling a sub panel in the out building. Approved buried cable or conduit is the best way to feed the structure. The grounds and neutrals in the sub panel should be on individual buss bars. Your local codes will dictate if any recepticles need to be GFCI protected. This should be done by use of a GFCI breaker unless only one exterior rec. need be protected. 

1)  220, 20A breaker for AC and/ or heat (use of a 220 unit is best for savings for both AC and heat)

2)  110, 20A breakers for recepticles (1 dedicated to all train equipment, the other for              Dehumidifier/ power tools and gereral purpose)

1 or 2) 110, 15A breakers for lighting (1 is actually sufficient, but it doesn't hurt to have a spare.

Even though these breakers/load totals 40 or 55A per buss on the sub panel this is within % of load for the main breaker/ disconnect in the house panel (40-50A).

Now this all depends on local codes and the combined total use of your main panel.

Your actual total Amp draw will never see the max of any of the breakers in the outbuilding panel for your intended use. (Unlees you decide to set a full wood shop, compressor etc)

 

Modeling B&O- Chessie  Bob K.  www.ssmrc.org

  • Member since
    July 2006
  • From: Vail, AZ
  • 1,943 posts
Posted by Vail and Southwestern RR on Wednesday, April 2, 2008 5:00 PM
The bottom line is that the trains will be a pretty insignificant portion of the equation.  You might want an extra light circuit compared to what you would normally have, but the power for the trains is in the noise!

Jeff But it's a dry heat!

  • Member since
    August 2004
  • From: Amish country Tenn.
  • 10,027 posts
Posted by loathar on Wednesday, April 2, 2008 4:15 PM
You might want to keep a dehumidifier in mind too.
  • Member since
    February 2008
  • 29 posts
Posted by ronmcc on Wednesday, April 2, 2008 3:43 PM
The room will have baseboard heat, AC mounted in the wall(7500btu/120volt), no coffee pot, small radio and trains. I have a seperate work shop with power tools. Shed is a mini barn style. I live in maryland on the eastern shore 7 miles south of the Chesapeak Bay Bridge. Do not need a building permit if less than 200sf.(will have 192sf).
  • Member since
    June 2003
  • From: CANADA
  • 2,292 posts
Posted by ereimer on Wednesday, April 2, 2008 2:40 PM
100 amp . that's enough to run a whole house unless you have central air , so it should be enough for a small railroad building . more will just add expense unless you really do need the extra power for a machine shop plus aircon plus electric heating for the winter . no point doing any less that 100 since you won't save enough to make a difference and you may want the extra in the future
  • Member since
    April 2003
  • 305,205 posts
Posted by Anonymous on Wednesday, April 2, 2008 2:31 PM
You've received excellent advice already, especially concerning installing more than you need.  One thing to remember, is that minimum code means exactly that.  It is the minimum that is required.  In my opinion, minimum is not near enough.It's important to install above what you need when everything is open to get to it.  Once you have an operating layout it's a pain to rip it out to get to electrical wiring.
  • Member since
    February 2002
  • 533 posts
Posted by CascadeBob on Wednesday, April 2, 2008 1:33 PM

I agree with what's been said.  Make a list of all the items that will be in the structure that draw power.  Consult with a licensed electrical contractor to get advice on how much capacity you'll need to run everything and then oversize it by a significant percentage.  It's cheaper to put in extra capacity now, with an adequate number of circuits for possible future use, than it is to try to put them in later.  If you plan to cover the electrical and other utilities in the walls, floor or ceiling, be sure to photograph all these things before they're covered.  Put a yard stick in each photo to give you a size scale in the photos.  Also you might consider marking on the floor the position of the centers of all the wall studs for future reference for attaching things to them.  This is a big help when you start drilling holes in your walls to attach bench work, etc.  I did this when I finished my train room and the photos have become invaluable in helping me to remember where the electrical wires and other things, like pipes, run in the walls.

Bob 

  • Member since
    October 2005
  • From: Northern Minnesota
  • 898 posts
Posted by colvinbackshop on Wednesday, April 2, 2008 12:57 PM

First of all...Welcome aboard.

Ryan and others have already asked good questions and I have a couple more that I see as necessary before I would feel comfortable in giving you an answer, other than a general blanket type answer.

You mentioned AC and heating: Will your heat be electric of some sort (resistance baseboard, stand alone ceramic...?) or would you just need a circuit for a blower or pump with the fuel source being gas, oil, wood...?? This will definitely be a major determine factor in the size of your distribution panel needed for the trainroom.

Another consideration would be: Will the panel for the trainroom be a sub-panel (being powered from an existing distribution panel) or will it have its power input from a main / meter loop? If it's a sub-panel, caution must be taken not to over load the panel that will be powering it.

So...With those two thoughts: Give thought to all the lighting you will want, along with the heating and cooling needs, add in the coffee pot (and what ever other creature comforts) and the power to run the layout. The most basic formula for this is simply adding together all of the amperage draws that you will have, determining the total and size a panel (amperage) that is appropriate for your codes.

For what ever it may be worth; here in MN the code reads that a lighting circuit is 15 amps and a utility circuit is a 20 amps. In my trainroom I have a 20 amp circuit for my "backshop" and gas fired furnace. Another 20 amp for all the transformers to power the total layout and three 15 amp circuits for lighting, all of which are from a 100 amp distribution panel.

Lastly...My rule of thumb is to oversize when possible. You just never know when you'll want or need some additional power...And boy, is it nice to already have that capability.

Puffin' & Chuggin', JB Chief Engineer, Colvin Creek Railway
  • Member since
    November 2007
  • From: Houston, Tx
  • 135 posts
Posted by ds137 on Wednesday, April 2, 2008 12:37 PM

Give us a few more specifics.

Where are you located?  warmer climates dictate more need for AC

how much insulation? built on slab or raised on blocks? other uses besides trains?

a well insulated building the size you describe can be kept comfortable with a

7k BTU AC window unit which will need at least a 20 amp 110 volt outlet.

bench top Table saw / circular saw will draw abt 15 amps

lighting - four 4' twin bulb flourescents abt 6 amps or each 100 watt bulb =1 amp

coffee pot - 7 or 8 amps brewing, 1 amp or less warming.  mini fridge abt 3 amps

More info can give you a better answer

Earl

 

I once caught a train in my pajama's. How it got in my pajama's I'll never know... (sorry, Groucho)

  • Member since
    July 2004
  • From: northern nj
  • 2,477 posts
Posted by lvanhen on Wednesday, April 2, 2008 12:24 PM
100 amp is generally the minimum code requirement for a structure (train shed or otherwise).  Depending on your location, you will probably need an electrical permit along with a building permit.  As a retired contractor, I can tell you that permits & inspections are for your own good & protection.  The codes are there to prevent fire, structural weakness, and other safety concerns.  Another concern is for insurance purposes.  In NJ, it is common for insurance companys to refuse to make payments for anything done without a permit when one was required.  Unless you have an old Tyco set running on a 4x8 with no scenery, you will need insurance, and this will probably require a "rider" to your current homeowners insurance.  My My 2 cents [2c]
Lou V H Photo by John
  • Member since
    August 2004
  • From: Amish country Tenn.
  • 10,027 posts
Posted by loathar on Wednesday, April 2, 2008 12:10 PM
I ran 100 amp 220v service to mine. I plan on running a 220v AC/heat strip/dehumidifier unit. I also want a 220v air compressor and welder. I've got 6 fluorescents, computer, stereo, TV, space heaters, fans, power tools. It's always better to have more power than you think you'll need.
  • Member since
    October 2007
  • From: Tennessee
  • 665 posts
Posted by Kenfolk on Wednesday, April 2, 2008 11:58 AM

Sign - Ditto [#ditto] on get qualified electrician. 

Otherwise could give new meaning to smokebox. 

  • Member since
    August 2002
  • From: Wake Forest, NC
  • 2,869 posts
Posted by SilverSpike on Wednesday, April 2, 2008 11:38 AM

I'm no electrician but it would depend on the total number of circuits you want in the room. 

Also, is the AC is 220 or 110, do you want separate lighting circuits for overhead or track lighting, separate lighting circuits for the sun up/sun down effect, etc....

I would make a list of all the items that will be running off electricity and then get a qualified electrician to consult with your requirements and needs.

Ryan Boudreaux
The Piedmont Division
Modeling The Southern Railway, Norfolk & Western & Norfolk Southern in HO during the merger era
Cajun Chef Ryan

  • Member since
    February 2008
  • 29 posts
Building a train room?
Posted by ronmcc on Wednesday, April 2, 2008 11:23 AM
I'm planning on building a train room in a 12'x16' insulated shed. What size braker box will I need to put in in order to run AC, Heat, lighting, coffee pot trains etc. I'm building in "N" scale.

Subscriber & Member Login

Login, or register today to interact in our online community, comment on articles, receive our newsletter, manage your account online and more!

Users Online

There are no community member online

Search the Community

ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT
Model Railroader Newsletter See all
Sign up for our FREE e-newsletter and get model railroad news in your inbox!