Trains.com

Subscriber & Member Login

Login, or register today to interact in our online community, comment on articles, receive our newsletter, manage your account online and more!

Convenience outlets around layout

3818 views
34 replies
1 rating 2 rating 3 rating 4 rating 5 rating
  • Member since
    August 2013
  • From: Richmond, VA
  • 1,890 posts
Convenience outlets around layout
Posted by carl425 on Sunday, May 27, 2018 9:38 AM

All the electrical code discussion has me wondering if what I did was kosher.

On my last layout I put a grounded plug on the end of a piece of Romex, then daisy chained 4 surface mount outlets around the front of the layout.  I mounted the outlets on the front of the web of my L-girders.  This was plugged in to a standard wall outlet like an extension cord.

Is this legit?  It was handy to have an outlet available close to where I was working so my plan was to do it again on the new layout.

I have the right to remain silent.  By posting here I have given up that right and accept that anything I say can and will be used as evidence to critique me.

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 9:51 AM

Since it's attached only to a piece of "custom furniture", it probably is.  If it were attached to be building, it would not be.

I do get the feeling from the description that it may not have been done as well as it should have been.  Photos would likely clear that up.

 

Ed

 

  • Member since
    August 2013
  • From: Richmond, VA
  • 1,890 posts
Posted by carl425 on Sunday, May 27, 2018 10:16 AM

7j43k
I do get the feeling from the description that it may not have been done as well as it should have been.  Photos would likely clear that up.

Sorry, no photos since the layout has been torn down.  The Romex was stapled every 12" or less to the rear girder (which was against the wall), then routed 90 degrees out to the outlets on the front and back to the rear for the run to the next outlet.  Wires to the outlet came through a 1" hole in the girder and into the back of the box.  The outer insulation of the Romex was always intact until it was inside the outlet box.  Conductors were stripped just enough to get under the screws of the receptacle - I don't trust the backstabbers).

I'm interested in whatever suggestions you have for next time.

I have the right to remain silent.  By posting here I have given up that right and accept that anything I say can and will be used as evidence to critique me.

  • Member since
    January 2014
  • From: Moneta, VA USA
  • 1,175 posts
Posted by gdelmoro on Sunday, May 27, 2018 10:29 AM

Is each outlet in an electrical box (metal better than plastic)? Is the Rome’s secured in the outlet box with a box connector? If so you’re good unless that particular circuit is now overloaded.  If it is one of the breakers in your house panel will be tripping.

Outlet box and cover

romex connector

Gary

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 10:44 AM

I'm noting here that I'm not endorsing what you're doing.

But.

You should be using romex clamps, as pictured above.

You should be running a ground wire to the metal box, and to the receptacle.

You should be doing everything in "a neat and workmanlike manner".

Get the book "Wiring Simplified".  Make sure anything you do doesn't violate the concepts you read about in the book.

The receptacle you're plugging this assembly into should be a GFI receptacle.

 

If you do all of that, I guess I can accept it.

 

 

Ed

 

PS:  If you're mounting the boxes onto a surface, don't use plastic plates, as in the picture above.  Use a Raco 864, or equivalent:

 

 

 

  • Member since
    January 2014
  • From: Moneta, VA USA
  • 1,175 posts
Posted by gdelmoro on Sunday, May 27, 2018 10:54 AM

I agree with the metal cover plate.  also, I’m assuming you know how to install wiring and outlets.  As ed points out you need to have proper grounds.

Gary

  • Member since
    August 2013
  • From: Richmond, VA
  • 1,890 posts
Posted by carl425 on Sunday, May 27, 2018 11:58 AM

7j43k
You should be using romex clamps, as pictured above.

I used these: (box and cover plate were all metal)

They have no provision for clamps, but I did staple the romex immediately behind the box on the back side of the girder.  Romex came into the box via the back punchout.

7j43k
You should be running a ground wire to the metal box, and to the receptacle.

Is that in addition to the ground that's included in the Romex?  I did connect that ground to the green screw on the receptacle. I made a loop in the bare wire and pinched it around the ground screw with needle nose while I tightened the screw. I thought that would work better for the daisy chain than cutting it and trying to put 2 ends under the screw.

7j43k
You should be doing everything in "a neat and workmanlike manner".

Always.

7j43k
The receptacle you're plugging this assembly into should be a GFI receptacle

Didn't think of that.  I'll do that next time.

Thanks.

I have the right to remain silent.  By posting here I have given up that right and accept that anything I say can and will be used as evidence to critique me.

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 12:19 PM

Regarding the Wiremold item in the photo:

They DO have a provision for a clamp.  In the very hole you ran through.  Look at the earlier photo of just such a clamp.

Wiremold makes varying depths of those boxes.  Be sure to get one deep enough to hold all the wire, wire nuts, and receptacle.  That one looks too shallow for my taste.

Regarding the grounding connection:

Best procedure is to have a ground wire attached to the box (there is a provision for a ground screw right there on the backplate) and to the receptacle.  Wire nut them to the incoming romex ground.

You NEVER put more than one wire under a screwhead.  NEVER!  And the wire wraps clockwise.  Only.

 

Be sure and get that book!  It is very good at basics.  Such as what I just discussed.

 

 

Ed

  • Member since
    January 2015
  • From: Southern California
  • 1,682 posts
Posted by Lone Wolf and Santa Fe on Sunday, May 27, 2018 12:47 PM

    Romex is for inside of walls. It is not meant for surface mounting. You can use wire mold boxes like pictured and the wire mold conduit to protect the wires. Or you can use metal handy boxes and steel flex to protect the wires. The covers can be plastic, that is ok. Protecting the wire is the important thing. Also make sure you have the proper gauge wire which matches the amperage of the circuit breaker: #12 wire for 20 amp breaker. #14 wire for a 15 amp breaker. You can use #12 wire for a 15 amp breaker since the wire is rated for a higher amperage.
    Chances are you were never in any danger with the way your romex was before but if it had gotten damaged by a sharp piece of sheet metal or a saw or another tool it could have been a problem.

Modeling a fictional version of California set in the 1990s Lone Wolf and Santa Fe Railroad
  • Member since
    July 2009
  • From: lavale, md
  • 4,640 posts
Posted by gregc on Sunday, May 27, 2018 12:48 PM

7j43k
PS:  If you're mounting the boxes onto a surface, don't use plastic plates, as in the picture above.  Use a Raco 864, or equivalent:

why?   is this required to meet code?

i'm thinking of doing something similar to carl so that I can control power to the layout with one switch.

greg - Philadelphia & Reading / Reading

  • Member since
    August 2013
  • From: Richmond, VA
  • 1,890 posts
Posted by carl425 on Sunday, May 27, 2018 12:59 PM

7j43k
They DO have a provision for a clamp.

The clamp wouldn't fit behind the receptacle. Good reason for a deeper box.

I have the right to remain silent.  By posting here I have given up that right and accept that anything I say can and will be used as evidence to critique me.

  • Member since
    September 2014
  • From: 10,430’ (3,179 m)
  • 2,277 posts
Posted by jjdamnit on Sunday, May 27, 2018 2:08 PM

Hello all,


Technically what your are doing is like adding power outlets to a home entertainment center. - -technically!

Practically you are opening yourself up to a fire hazard.

I've seen some pretty scary installations similar to your situation.

What is the breaker rated for that you are plugging into- -15A, 20A?

What else is on this circuit?

I understand these are "convenience" outlets. What will you be powering and what is the potential max amperage load?

If this were my project I would:

  • Put a breaker box between the wall outlet and the layout, attached to the layout.
  • I would also under rate this breaker; 20A service 15A breaker, 15A service 10A breaker.
  • Use 12/3 electrical wire SJOOW jacket 20A with the appropriate plug from the wall outlet to the breaker box on the layout.
  • Use non-metalic PVC pipe or non-metalic Conduit to run the wires from the breaker box to the switch/outlet boxes with appropriate fittings.
  • I would use individual wires: solid core 12ga; Black, White & Green, rather than Romex®.
  • Plastic switch/outlet boxes and covers on the layout.
  • 15A wall outlets with ground (GFI to be extra safe).

Or...

An extension cord from the wall to what ever you are using. If you need more outlets you can put a power strip on the end.

Much cheaper and safer.

Hope this helps.

 

"Uhh...I didn’t know it was 'impossible' I just made it work...sorry"

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 2:11 PM

gregc

 

 
7j43k
PS:  If you're mounting the boxes onto a surface, don't use plastic plates, as in the picture above.  Use a Raco 864, or equivalent:

 

why?   is this required to meet code?

i'm thinking of doing something similar to carl so that I can control power to the layout with one switch.

 

 

No.  The ones I cited are smaller, and hang over the edge less.  They often come with rounded corners, so they're less "pointy".  And, being made of steel, they won't tend to break.  Like plastic.

Another option instead of using the Wiremold boxes is to use regular 4 square boxes, such as a Raco 190:

 

And then use one of these covers:

 

 

They are Raco 902C and 907C, respectively.  You'll get a good amount of room inside, they're quite sturdy, and the assembly will be 2 1/8" thick--thinner than if you use a switch box.

 

Ed

 

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 2:17 PM

jjdamnit

 

  • I would use individual wires: solid core 12ga; Black, White & Green, rather than Romex®. 

 

No.  The outer sheathing of the romex will help protect the wires.  And thus you.  This is 120V.

Even better would be to use flexible steel conduit.  It's bendy, so it's easy to install. And it will do a better job of protecting the conductors.

 

 

 

Ed

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 2:33 PM

Still another way to go is with something like Plugmold:

 

It comes in various lengths, and with or without a plug and cord.

 

Ed

  • Member since
    July 2009
  • From: lavale, md
  • 4,640 posts
Posted by gregc on Sunday, May 27, 2018 2:33 PM

jjdamnit
Practically you are opening yourself up to a fire hazard.

how?   would this be a problem if you use romex?

and how much current at 120V are you likely to draw.   A 10A booster supplying 15V is only 150W or 1.25 A at 120V.

 

7j43k
Even better would be to use flexible steel conduit

by this you mean BX cable?  I thought the purpose of BX cable is to protect workers who might be cutting through walls during demolition who might cut through an unintentionally live cable.   why would BX be better?   it has a limited radius

 

i was thinking of nailing up some blue plastic electrical boxes on the backside of the L-girders connecter with romex and use a 3-prong power cord from an old microwave  to connect to a wall outlet.

greg - Philadelphia & Reading / Reading

  • Member since
    January 2009
  • From: Maryland
  • 12,853 posts
Posted by ATLANTIC CENTRAL on Sunday, May 27, 2018 2:40 PM

7j43k

I'm noting here that I'm not endorsing what you're doing.

But.

You should be using romex clamps, as pictured above.

You should be running a ground wire to the metal box, and to the receptacle.

You should be doing everything in "a neat and workmanlike manner".

Get the book "Wiring Simplified".  Make sure anything you do doesn't violate the concepts you read about in the book.

The receptacle you're plugging this assembly into should be a GFI receptacle.

 

If you do all of that, I guess I can accept it.

 

 

Ed

 

PS:  If you're mounting the boxes onto a surface, don't use plastic plates, as in the picture above.  Use a Raco 864, or equivalent:

 

 

 

 

Ed, are we assuming it is in a basement? The OP did not sare the layout location with us. I ask regarding the need for a GFCI?

And those rules have "progressed" over the years........

Sheldon

    

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 2:49 PM

gregc

 

7j43k
Even better would be to use flexible steel conduit

 

by this you mean BX cable?  I thought the purpose of BX cable is to protect workers who might be cutting through walls during demolition who might cut through an unintentionally live cable.   why would BX be better?   it has a limited radius

 

No.  Flexible steel conduit looks like big BX, and it comes empty.  You add your own wire.  BX would probably work too.  Or MC.

No.  BX is not to protect workers who.....      It is designed for exposed work.  Romex can only be installed exposed if it cannot receive physical damage.  Around here, that's interpreted to mean "hardly ever".

 

i was thinking of nailing up some blue plastic electrical boxes on the backside of the L-girders connecter with romex and use a 3-prong power cord from an old microwave  to connect to a wall outlet.

 

 

Get yourself a copy of "Wiring Simplied".  First.

 

Ed

  • Member since
    July 2009
  • From: lavale, md
  • 4,640 posts
Posted by gregc on Sunday, May 27, 2018 2:55 PM

7j43k
Get yourself a copy of "Wiring Simplied".  First

does this apply to non-house wiring, the topic of this thread?

i've wired up a garage, inspected by the town

greg - Philadelphia & Reading / Reading

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 2:58 PM

Sheldon,

My recollection is the layout will be a piece of custom furniture.  And that the "furniture" was going to plug into a (perhaps newly installed) GFI receptacle.  Not so much because of potential dampness, but more along the lines of it's a sort of "workshop".  GFI's are better than not-GFI's.

I suppose we could get into AFCI's, too.  In fact, I think we should.  EVERYONE!!!  The GFI receptacle I said to install has turned into this:

https://www.amazon.com/Leviton-AGTR1-W-SmartlockPro-Function-Receptacle/dp/B01CG8MP9W/ref=sr_1_1_sspa?ie=UTF8&qid=1527451033&sr=8-1-spons&keywords=afci+receptacle&psc=1

Do it!

Also, I'm not gonna be there to supervise the electrical installation.  And I don't know whether it will be done to perfection.  Etc. Etc.

I'm approaching this as:  they're gonna do it, anyway.  let's try to make it better.

 

Ed

 

  • Member since
    August 2013
  • From: Richmond, VA
  • 1,890 posts
Posted by carl425 on Sunday, May 27, 2018 4:57 PM

jjdamnit
I understand these are "convenience" outlets. What will you be powering and what is the potential max amperage load?

These outlets are for working on the layout.  There location would make them unsightly to leave things plugged in all the time.  As highly skilled as I am, I can still only operate one tool at a time in a single location.

Worst case would be track laying where I'm using a Dremel while my 35-watt soldering iron is plugged in.

This outlet is one of only two that is on an extra 15-amp circuit I had installed when my office and train room were son's and daughter's bedrooms.  She had a habit of plugging in a hair straightening iron while running a blowdrier with CRT TV's on in both bedrooms.

Today the outlet in my office supports the UPS that runs the computer, monitor, Ethernet switch, speakers and my Sprog :).  With the music playing the UPS reports a load of 144 watts.

I have the right to remain silent.  By posting here I have given up that right and accept that anything I say can and will be used as evidence to critique me.

  • Member since
    August 2013
  • From: Richmond, VA
  • 1,890 posts
Posted by carl425 on Sunday, May 27, 2018 5:09 PM

7j43k
My recollection is the layout will be a piece of custom furniture.  And that the "furniture" was going to plug into a (perhaps newly installed) GFI receptacle.  Not so much because of potential dampness, but more along the lines of it's a sort of "workshop".  GFI's are better than not-GFI's.

I thought the GFCI recommendation was because of the wet scenery materials.

BTW, one of the main reasons for this "power strip/entension cord/wired furniture" was to avoid climbing under the benchwork.  Instead of a GFCI outlet at the wall, how about a GFCI as the first outlet in my chain?

I have the right to remain silent.  By posting here I have given up that right and accept that anything I say can and will be used as evidence to critique me.

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 6:55 PM

carl425

 

 
7j43k
My recollection is the layout will be a piece of custom furniture.  And that the "furniture" was going to plug into a (perhaps newly installed) GFI receptacle.  Not so much because of potential dampness, but more along the lines of it's a sort of "workshop".  GFI's are better than not-GFI's.

 

I thought the GFCI recommendation was because of the wet scenery materials.

 

Nope.  It's there to keep you from getting electrocuted if you make a mistake.  With or without water present.

BTW, one of the main reasons for this "power strip/entension cord/wired furniture" was to avoid climbing under the benchwork.  Instead of a GFCI outlet at the wall, how about a GFCI as the first outlet in my chain?

 

 
No.  I want your entire self-created system plugged into a GFI.  Or, more properly, the AFCI/GFI thingy I linked to.
 
 
Ed
 
 

 

 

 

  • Member since
    March 2015
  • 1,358 posts
Posted by SouthPenn on Sunday, May 27, 2018 9:43 PM

First, every locality has it's own rules for electrical wiring. Quoting rules is fruitless.

Safety is different. If the Romex is under the layout and not easily accessible, it should be fine. Use caution when drilling into your layout, you could hit the wires. But you can hit the Romex in walls too. Using BX is overkill and is usually required in commercial buildings. 

Using plastic boxes and covers is fine if it passes local rules. You cannot get shocked or electrocuted from plastic so there is no grounding required. If you believe you will be smashing the covers and boxes, then use metal. But make sure they are properly grounded.

Duplex receptacles are rated at 1.5 amp for calculating how many you can have on one breaker. A 15 amp breaker can have 10 duplex receptacles on it. Something that is plugged into a receptacle is not counted. But with your multiple outlets on a plug, it would be a judgment call by the inspector. Most would consider it an extension cord. If you use Wiremold and it is hard-wired into the circuit, then it is counted.

You could change the standard breaker to a GFCI or AFCI for another layer of protection. If you have older power tools with brushes, the AFCI might become a nuisance. The 'A' in AFCI is for arching which the old power tools do plenty of.

 

South Penn
  • Member since
    January 2009
  • From: Maryland
  • 12,853 posts
Posted by ATLANTIC CENTRAL on Sunday, May 27, 2018 10:02 PM

SouthPenn

Duplex receptacles are rated at 1.5 amp for calculating how many you can have on one breaker. A 15 amp breaker can have 10 duplex receptacles on it. Something that is plugged into a receptacle is not counted. But with your multiple outlets on a plug, it would be a judgment call by the inspector. Most would consider it an extension cord. If you use Wiremold and it is hard-wired into the circuit, then it is counted. 

WRONG, we just went through this in another thread, "power for new layout room".

While state and local goverments can and do create their own exceptions, the foundation is all based on the NEC.

NOTHING in the NEC limits the number of receptacles on a 15 amp or 20 amp circuit breaker. The limitation is how many square feet of the building each circuit can supply with general power.

Go to that thread and read what I posted, then go find a copy of the NEC and learn it before you go giving advice. In that thread I posted the applicable NEC articles, you can look it up.

Sheldon

    

  • Member since
    May 2004
  • 7,500 posts
Posted by 7j43k on Sunday, May 27, 2018 11:23 PM

SouthPenn

First, every locality has it's own rules for electrical wiring. Quoting rules is fruitless.

I'll be sure to tell that to the next electrical inspector who quotes me a rule.

Using BX is overkill and is usually required in commercial buildings. 

 

No, it is not usually required in commercial buildings.
 
See Article 320 of the NEC. 
 
 
 
Ed
  • Member since
    March 2015
  • 1,358 posts
Posted by SouthPenn on Monday, May 28, 2018 9:11 AM

7j43k

 

 
SouthPenn

First, every locality has it's own rules for electrical wiring. Quoting rules is fruitless.

 

 

I'll be sure to tell that to the next electrical inspector who quotes me a rule.

 

 

Using BX is overkill and is usually required in commercial buildings. 

 

 

 

 

No, it is not usually required in commercial buildings.
 
See Article 320 of the NEC. 
 
 
 
Ed
 

Maybe I should have been more specific. Quoting rules on this forum is fruitless as I don't know where the poster lives.

The commercial buildings and offices I worked on were inside city limits. They had their own rules. And working in government-owned buildings was like working on another planet. They had their own way of doing things. Even the local townships have their own rules. But that was over 40 years ago. Times have changed. It's gotten worse.

South Penn
  • Member since
    January 2009
  • From: Maryland
  • 12,853 posts
Posted by ATLANTIC CENTRAL on Monday, May 28, 2018 10:47 AM

SouthPenn

 

 
7j43k

 

 
SouthPenn

First, every locality has it's own rules for electrical wiring. Quoting rules is fruitless.

 

 

I'll be sure to tell that to the next electrical inspector who quotes me a rule.

 

 

Using BX is overkill and is usually required in commercial buildings. 

 

 

 

 

No, it is not usually required in commercial buildings.
 
See Article 320 of the NEC. 
 
 
 
Ed
 

 

 

Maybe I should have been more specific. Quoting rules on this forum is fruitless as I don't know where the poster lives.

The commercial buildings and offices I worked on were inside city limits. They had their own rules. And working in government-owned buildings was like working on another planet. They had their own way of doing things. Even the local townships have their own rules. But that was over 40 years ago. Times have changed. It's gotten worse.

 

SouthPenn,

Commerical and industrial work is a whole different world than residential work - both then and now.

A few noteable examples of local rules that are stricter than the NEC:

City of baltimore - ALL commercial buildings are wired in EMT or armored cable (not bx).

City of Chicago (Cook County) - not sure if it is still this way, but at one time ALL buildings had to be wired in EMT or Armored Cable.

Both of the cities above have one thing in common - they both burned to the ground in the early days of electricity.

But none of that has anything to do with some guy who needs a few receptacles in his train room.

Sheldon

    

  • Member since
    December 2004
  • From: Bedford, MA, USA
  • 21,336 posts
Posted by MisterBeasley on Monday, May 28, 2018 10:52 AM

I prefer to use solid, wall mounted recepticles.  I always find that when inserting or removing plugs from bench mounted recepticles, the resulting pressure tends to pull the benchwork in or out a bit.  I like my plugs more solid.

When working around my layout, I use a large, heavy extension cord to reach the wall-mounted outlets.

It takes an iron man to play with a toy iron horse. 

  • Member since
    August 2013
  • From: Richmond, VA
  • 1,890 posts
Posted by carl425 on Monday, May 28, 2018 1:50 PM

MisterBeasley
prefer to use solid, wall mounted recepticles.  I always find that when inserting or removing plugs from bench mounted recepticles, the resulting pressure tends to pull the benchwork in or out a bit. 

I would never tolerate benchwork that would move under the force required to insert or remove a plug from a receptacle.

I have the right to remain silent.  By posting here I have given up that right and accept that anything I say can and will be used as evidence to critique me.

Subscriber & Member Login

Login, or register today to interact in our online community, comment on articles, receive our newsletter, manage your account online and more!

Users Online

There are no community member online

Search the Community

ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT
Model Railroader Newsletter See all
Sign up for our FREE e-newsletter and get model railroad news in your inbox!