Fuses/circuit breakers for LED strip lighting?

8483 views
12 replies
1 rating 2 rating 3 rating 4 rating 5 rating
  • Member since
    July 2006
  • From: Bradford, Ontario
  • 15,797 posts
Fuses/circuit breakers for LED strip lighting?
Posted by hon30critter on Wednesday, January 6, 2016 1:13 AM

More questions from he who knows just about nothing re electricity.Smile, Wink & Grin This time I'm asking about circuit breakers for the LED strips.

I have ordered a total of 10 x 5m 5630 natural white LED strips with 60 LEDs/m. The draw will be 5 amps @ 12 volts per 5m strip. I will be feeding the strips from two 36 amp x 12 volt power supplies with 5 strips per power supply.

Do I need to install circuit breakers or fuses for each of the 5m strips? I suspect the answer is "YES, idiot..." but I'm having trouble finding the right components.

Any suggestions?

Thanks

Dave

I'm just a dude with a bad back having a lot of fun with model trains, and finally building a layout!

  • Member since
    August 2011
  • From: A Comfy Cave, New Zealand
  • 6,252 posts
Posted by "JaBear" on Wednesday, January 6, 2016 3:42 AM
Some light reading Dave.

http://www.optifuse.com/PDFs/FuseSelectionGuide_RevA.pdf

Cheers, the Bear, whose definite knowledge of electricity is that he has been a good ground from time to time! Lightning Sigh

"One difference between pessimists and optimists is that while pessimists are more often right, optimists have far more fun."

  • Member since
    February 2002
  • From: Reading, PA
  • 30,002 posts
Posted by rrinker on Wednesday, January 6, 2016 6:55 AM

 Yes, you should fuse each run. The products I linked are nice distribution blocks that take auto type fuses, and an auto fuse form factor 5 amp circuit breaker. The one I linked breaks the input up into 4 or 6 fused outputs, but they have bigger ones as well. That's probably the easiest way to go without rolling your own breaker panel.

                   --Randy

 


Modeling the Reading Railroad in the 1950's

 

Visit my web site at www.readingeastpenn.com for construction updates, DCC Info, and more.

  • Member since
    October 2005
  • From: Detroit, Michigan
  • 2,284 posts
Posted by Soo Line fan on Wednesday, January 6, 2016 9:47 AM

If your load is 5 A, a 7.5 A twin blade automotive fuse would work well for each branch. 

Jim

  • Member since
    December 2004
  • From: Pa.
  • 3,361 posts
Posted by DigitalGriffin on Wednesday, January 6, 2016 10:39 AM

Depends if you want one strip to go out versus all of them.  Sort of like if you want the one block on your layout to go down, versus all of them.

Since your supply current is close to demand + small overhead, you just need to divide the current by 5.  (one for each strip)  

Fuse rating = ((Supply Current / 5)*1.1 (10% overhead for small surges) for each LED strip.  

So each led strip will be roughly 7 * 1.1 = ~7.7 amps per strip 

 

So Jim (Soo Line) has it about right.

Use a slow blow fuse as so it doesn't trip during startup.

Don - Specializing in layout DC->DCC conversions

Modeling C&O transition era and steel industries There's Nothing Like Big Steam!

  • Member since
    July 2006
  • From: Bradford, Ontario
  • 15,797 posts
Posted by hon30critter on Wednesday, January 6, 2016 5:36 PM

Randy:

I didn't see a link in your post.

Thanks

Dave

I'm just a dude with a bad back having a lot of fun with model trains, and finally building a layout!

  • Member since
    July 2006
  • From: Bradford, Ontario
  • 15,797 posts
Posted by hon30critter on Wednesday, January 6, 2016 5:38 PM

Thanks Bear.

I now have a better understanding of the theory.

Dave

I'm just a dude with a bad back having a lot of fun with model trains, and finally building a layout!

  • Member since
    July 2006
  • From: Bradford, Ontario
  • 15,797 posts
Posted by hon30critter on Wednesday, January 6, 2016 5:40 PM

Jim and Don:

Thanks for doing the math.

Dave

I'm just a dude with a bad back having a lot of fun with model trains, and finally building a layout!

  • Member since
    February 2002
  • From: Reading, PA
  • 30,002 posts
Posted by rrinker on Wednesday, January 6, 2016 6:42 PM

hon30critter

Randy:

I didn't see a link in your post.

Thanks

Dave

 

In the wire thread

These:  http://www.amazon.com/Blue-Sea-Systems-Blade-Block/dp/B000THQ0CQ/ref=pd_sim_200_3?ie=UTF8&dpID=51%2B5nXsWtYL&dpSrc=sims&preST=_AC_UL160_SR123%2C160_&refRID=0TXR93P5DSV6JV3VE8R1

Then you can get either fuses or resettable circuit breakers that plug in. This one breaks the input up into 6 fused circuits, but they have bigger ones as well (but 6x 5 amp circuits is about as much as you'd want to put on a single 36 amp power supply).

 Or for cheap, and just tack the wires to a board with some terminal strips, there are these fuse holders for auto type fuses/circuit breakers:

http://www.amazon.com/Bullz-BATC10-10-Gauge-In-Line-Holder/dp/B00NQ8F242/ref=pd_sim_263_3?ie=UTF8&dpID=61VvWWdsNzL&dpSrc=sims&preST=_AC_UL160_SR153%2C160_&refRID=01E8JKQEAMZCZFA83Z3J

Just add some terminal strips and you are basically making your own version of the first item.

           --Randy

 


Modeling the Reading Railroad in the 1950's

 

Visit my web site at www.readingeastpenn.com for construction updates, DCC Info, and more.

  • Member since
    October 2005
  • From: Detroit, Michigan
  • 2,284 posts
Posted by Soo Line fan on Wednesday, January 6, 2016 8:25 PM

The one Randy has referenced is known as a ATO/ATC size fuse and is shown on the left. These replaced glass fuses in the late 70s in autos and were used up to the mid to late 90s.

The size on the right is know as a mini fuse and has replaced the ATO/ATC style. Both can be found just about anywhere but they are not interchangeable.

Breaking up a system is more work but is easier to diagnose if a fault occurs. Imagine a home or car with only one circuit breaker. Where do you begin Sigh

Jim

  • Member since
    July 2006
  • From: Bradford, Ontario
  • 15,797 posts
Posted by hon30critter on Wednesday, January 6, 2016 8:49 PM

Hi Randy:

Sorry, somehow I missed your last post on the wire gauge thread.

Dave

I'm just a dude with a bad back having a lot of fun with model trains, and finally building a layout!

  • Member since
    July 2006
  • From: Bradford, Ontario
  • 15,797 posts
Posted by hon30critter on Wednesday, January 6, 2016 8:50 PM

Jim:

Thanks for explaining the fuse styles.

Dave

I'm just a dude with a bad back having a lot of fun with model trains, and finally building a layout!

  • Member since
    July 2006
  • From: Bradford, Ontario
  • 15,797 posts
Posted by hon30critter on Wednesday, January 6, 2016 11:05 PM

Problem solved. I just ordered two x 6 position ATC style fuse holders like these:

http://www.amazon.ca/Docooler%C2%AE-Circuits-Blade-Holder-Vehicle/dp/B00V65PLAC/ref=sr_1_3?ie=UTF8&qid=1452143301&sr=8-3&keywords=Docooler+32v+fuse+holder

Thanks for everyone's help.

Dave

I'm just a dude with a bad back having a lot of fun with model trains, and finally building a layout!

Subscriber & Member Login

Login, or register today to interact in our online community, comment on articles, receive our newsletter, manage your account online and more!

Users Online

There are no community member online

Search the Community

ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT
Model Railroader Newsletter See all
Sign up for our FREE e-newsletter and get model railroad news in your inbox!